0-10v Float switch

  • Thread starter Thread starter BigAsh
  • Start date Start date
  • Tagged users None

Users Who Are Viewing This Thread (Total: 0, Members: 0, Guests: 0)

BigAsh

New member
Joined
Apr 30, 2022
Messages
9
Reaction score
0
Location
Florida
I have soldered a gx12 6 pin connector to 2 wires on a float switch. I can’t seem to get it to work. Float has been checked and has around 2.5v when closed. But when open it doesn’t change status. Almost like it’s getting constant voltage regardless.
 

Attachments

  • F45F48A1-CDAC-46D7-B5C7-0551CFF9ACB0.jpeg
    F45F48A1-CDAC-46D7-B5C7-0551CFF9ACB0.jpeg
    238.7 KB · Views: 3
Use the 0-10V Diagnostics Input to determine the voltage when wet and dry. Then change the range so that the lower number is OUTSIDE the range.

 
I have never used pin 3. I go from the input pin to ground or pin 6 with the switch, If fact for float switches i connect them to the sense port. Those 6 pin on GX connectors very close to each other. I usually get the quad cable and then connect with a 3.5 mm jack instead of trying to create my own cable.
 
I have never used pin 3. I go from the input pin to ground or pin 6 with the switch, If fact for float switches i connect them to the sense port. Those 6 pin on GX connectors very close to each other. I usually get the quad cable and then connect with a 3.5 mm jack instead of trying to create my own cable.
I did originally connect to the sense and it worked fine, but I needed one more port and figured try it on the 0-10, so based on what your saying you wouldn’t need the 5v supply? My understanding is pin 3 is 5v then the pin one would be the input, so I am assuming and may have this wrong but I would think when the switch is closed pin one would sense 5v and when open 0. Didn’t think it needed ground.
 
Use the 0-10V Diagnostics Input to determine the voltage when wet and dry. Then change the range so that the lower number is OUTSIDE the range.

Thank you, I have done this and my voltage does not change in open or closed. When I pin out my connector it does show the switch is operating correctly but I don’t see a voltage drop when connected.
 
The inputs float open at around 2.5v. They do not go to 0 unless you add a switch from the pin to ground. You can setup the input to measure the voltage. Carlos posted a link on how to do this for you. If do that then you can see what the input is doing when you open and close the switch.
 
The inputs float open at around 2.5v. They do not go to 0 unless you add a switch from the pin to ground. You can setup the input to measure the voltage. Carlos posted a link on how to do this for you. If do that then you can see what the input is doing when you open and close the switch.
Thank you I will try this
 
The inputs float open at around 2.5v. They do not go to 0 unless you add a switch from the pin to ground. You can setup the input to measure the voltage. Carlos posted a link on how to do this for you. If do that then you can see what the input is doing when you open and close the switch.
Thank you for this info, everything is working now
 