  1. JeffB418

    Full DIY Hydros Pinout Cheat Sheet

    This might work HYDROS Drive Port Cable you might have to adapt the 5.5mm x 2.1mm barrel connector to another type if it doesnt fit. These types of kits can do that adapting Amazon.com
  2. JeffB418

    Auto Top Off Control, Using One 0-10V Input

    Doing with your resistor tree, would look something like this I suppose. Green are valid states. Red are invalid. 0.2V margin between valid and invalid states could be tight, but not impossible.
  3. JeffB418

    Auto Top Off Control, Using One 0-10V Input

    You could do something like this: Gives you decent margin between normal states, 0.2V all open, 1.7V low closed, 3V low/med closed, 5V low/med/high closed. And also allows you to detect the case where the middle (most important) float has gotten stuck closed with a 2.5V output. I had to put...
  4. JeffB418

    Auto Top Off Control, Using One 0-10V Input

    Also simulate the situations where a float switch fails to close before a higher level switch does. you do not want 2 situations to generate the same output voltage, because then you wouldnt be able to tell what the actual state of the system is. Pulling the input to ground with a resistor also...
  5. JeffB418

    Auto Top Off Control, Using One 0-10V Input

    The mode control inputs are snapped 1V increments with auto rounding up/down. IE 1.4V will trigger a 1V mode select. But if you just make an analog 0-10V input, you can scale the voltage up using the scale factor and have more fine resolution for your application. Use the Data type generic. IE...
  6. JeffB418

    Alarm Logging

    When you generate an alert output, detail in the log what caused the alert. To make it easier to track down alarms. Instead of just off/on, put what causes it to turn on.
  7. JeffB418

    Reorder Collective/Devices

    In the left menu, make it able to reorder devices or collectives.
  8. JeffB418

    Full DIY Hydros Pinout Cheat Sheet

    There might be 2 issues, 1) you might have the pump connected wrong, i personally dont have any exp with red sea pumps or connecting them to kraken since they use a non-standard connector but 2) you likely exceeding your Kraken's max load. You said you have 4 XR15's connected already. Each of...
  9. JeffB418

    Switch Input on Sense Port

    No. One sensor per sense port.
  10. JeffB418

    Can the Hydros control Kessil lights?

    AP9X are not 0-10V controllable. They do not have input ports, only output ports.
  11. JeffB418

    Automatic Feeder wifi-less

    They discuss it in the manual here Plank Autofeeder Support Page
  12. JeffB418

    Cycling on and off

    use the output type advanced => generic Use internal schedule and enable advanced:
  13. JeffB418

    X4 Ports Salt Creep?

    Reach out to support@coralvue.com, they do offer repair services for items even out of warranty
  14. JeffB418

    No ability to unkink tubing or calibrate from tile…

    Yeah its a safety backup so that you dont accidently run calibration during a dosing schedule by mistake
  15. JeffB418

    XP8 showing incorrect wattage

    Reach out to support@coralvue.com and they can investigate whats going on
  16. JeffB418

    Water sensors not working

    reach out to support@coralvue.com and someone can help you directly.
  17. JeffB418

    IV Schedule issues with new Firmware

    External schedules don’t have days of week anymore.
  18. JeffB418

    IV Schedule issues with new Firmware

    I let engineering know about this and they are looking into why it was changed.
  19. JeffB418

    Firmware 341 / App 3.0.2 (303)

    Immediately contact support at support@coralvue.com
  20. JeffB418

    Firmware 341 / App 3.0.2 (303)

    A fix is coming shortly for this.
Back
Top