I'd like to set up an ATO using dual float switches instead of an electronic level sensor. I know how to setup float switches on the 0-10v input and I know I can use a float switch as a low level indicator to turn on/off a reservoir pump. What I don't see is how to setup a high level float switch to shutdown the pump in case of a malfunction.
I did look through the RODI filter section but I'm unsure if that's a way I can setup my ATO with an emergency off float switch. Has anyone had some experience using dual float switches on an ATO?
Thanks.
 
You must change the ATO output to Generic and use two inputs. Make the Generic output active when input 1 AND input 2 are "dry."
 
Too easy! Got it. I have not found any input or output that the Hydros was unable to accommodate.
Thanks much.
 
Too easy! Got it. I have not found any input or output that the Hydros was unable to accommodate.
Thanks much.
You can also change the tile icon to the ATO icon if you want to do that on that generic output.
 