After having problems with float switches getting gunked up and sticking, fleece being advanced too rapidly and wasted, and fleece jams causing motor stalls that go unchecked, I decided to ditch the mechanical float switches and drive the fleece motor directly from a Hydros Drive Port.
Float switches don't turn OFF until the water level drops, and that can take several seconds, wasting fleece. With Hydros control you can force the fleece chamber water level to sit at/near the bypass for some time before you allow it to advance. And you can control precisely (in 1-second increments) how much fleece is advanced each time.
Using a single Hydros Water Level Sensor in the fleece chamber to sense when/where the water level rises at/near the bypass, along with a simple custom cable from Drive Port-1 to the fleece motor, this is what I setup...
A Generic output runs a schedule (1-minute iterations) with AND logic from the water sensor input. Schedule ON + Sensor WET = trigger ON
If the water sensor is DRY then the output remains OFF. The output Drive Port-1/fleece motor is only engaged at the 1-minute mark AFTER the sensor goes WET.
If the water sensor remains WET after one fleece advance of 1-second, then it will not advance again until the 1-minute schedule trigger rolls around again.
The amount of fleece advanced each time is controlled by the Run How Long parameter.
Power monitoring with an Orange Alert is also set on the Combiner in case fleece gets jammed and the motor stalls. Typical motor current is 0.4-0.6 watts. I set 0.8 as the stall current threshold for the alert.
Float switches don't turn OFF until the water level drops, and that can take several seconds, wasting fleece. With Hydros control you can force the fleece chamber water level to sit at/near the bypass for some time before you allow it to advance. And you can control precisely (in 1-second increments) how much fleece is advanced each time.
Using a single Hydros Water Level Sensor in the fleece chamber to sense when/where the water level rises at/near the bypass, along with a simple custom cable from Drive Port-1 to the fleece motor, this is what I setup...
A Generic output runs a schedule (1-minute iterations) with AND logic from the water sensor input. Schedule ON + Sensor WET = trigger ON
If the water sensor is DRY then the output remains OFF. The output Drive Port-1/fleece motor is only engaged at the 1-minute mark AFTER the sensor goes WET.
If the water sensor remains WET after one fleece advance of 1-second, then it will not advance again until the 1-minute schedule trigger rolls around again.
The amount of fleece advanced each time is controlled by the Run How Long parameter.
Power monitoring with an Orange Alert is also set on the Combiner in case fleece gets jammed and the motor stalls. Typical motor current is 0.4-0.6 watts. I set 0.8 as the stall current threshold for the alert.