Danny
HYDROS Expert
Also, when you set the min and max on the schedule they will fit within the min and max set on the pump. so 1% on the schedule will actually be the min setting you set for the pump. And 100% would be the max set on the pump output. Check the voltage at one of the outputs that is working and compare them with one of the outputs that does not work. Since they are setup the same the voltages in each mode should be close to the same. If they are it sounds like an issue somewhere other than the controller if a good working output and one that does not appear to work output almost the same voltages in the same modes. Make sure you voltage Is positive and not negative on the meter since you are connecting the black probe to the ground of the plug.