I use a Brute trash can as my DI storage for ATO. It is automatically refilled when it goes low. I copied this from my Build thread on R2R. Hope this is a help.
Below is a screenshot of the settings for the DI tank. The only one I will use on this is the Feed Output Device. It is the DI fill solenoid between the RODI unit and the DI tank. The other two outputs I don't currently have. The next setting is the high level input. This is the full sensor on the tank that is to be refilled. The next setting is the Low Level Input. This is the sensor that will start the fill sequence in the tank being filled. The next input is the Leak Detector Input. If you have a single leak detector at you RODI station and storage tank you can select that detector here. I have two sensors so I used the Depends On settings to do the same thing.
View attachment 1922
The next setting is the Depends On setting. It is set to Leak Garage. That output is a combination of the RODI leak detector and AC leak detector. The Detector under the AC is within a few feet of the RODI unit and the storage tanks. So I use it as a backup for the RODI detector. The dependency mode is off if on. I have the advanced settings enabled. I did this so I can set the Feed Maximum On Time. I set this to 4 hours. I am going to see if that shorter time frame is ok. Feed Run Past Max On Time is set to off. I want it to turn off it it goes that long and is still on. Notification level is set to orange. That way I will get an alert if it runs too long. This will create three Tiles in outputs but all lead to these same settings. It is split into three outputs so there is an indicator for all three.